Support / FAQs / About techtown

Home Forums Archives I have an very Intermittent problem with a Maxx Cold MXM2-48R

  • I have an very Intermittent problem with a Maxx Cold MXM2-48R

    Posted by guest on February 12, 2018 at 12:00 am

    The refrigeration unit will stay for days to over a week at the 36 degree set point, then randomly will go below freezing. I suspect the Thermostat and would like to know if anyone else has seen this same problem before I order it.

    partsgirl replied 5 years, 6 months ago 1 Member · 8 Replies
  • 8 Replies
  • fixbear

    Member
    February 12, 2018 at 6:51 pm

    That cooler uses a Dixel digital cold control. So what is causing your problem,  I suspect the thermistor connections are not secure to the controller or the thermal stresses of the evaporator is effecting the accuracy of the thermistor.  What it comes down to is the controller is seeing a resistance that is higher than the  evaporator’s real temperature.

     

    One other item that may cause it, the thermistor bonding to the evaporator coil.  The coil in a cooler has to get down to between 14 and 19 degrees before the compressor stops to get the box to temp . Called take down. Most evaporator take down’s are about 15 degrees F   If the bonding clamp is loose, it will read box temp instead of coil temp.

     

    Do you have any trouble codes?  Like a P2?

  • henlopen

    Member
    April 13, 2018 at 3:30 pm

    No trouble codes, and since your reply, the unit has only done it one other time.  Sorry for the delay in replying, I was hoping to have more to report.  Will keep checking on it.  Thanks Very Much!

  • fixbear

    Member
    April 13, 2018 at 4:42 pm

    Make sure to verify with a independent calibrated thermometer that the box temp is indeed freezing and not a reading error.  Note to cooling light and fan lights if lit or not. I want to make sure you have a manual for the controller. to you can rad any codes and set the low temp alarm.

    http://www.maxximumfoodservice.com/pages/en/Manuals/Manual%20for%20Glass%20D_MXM1-12-16-23RF_MXM2-48R_FRS-MXM3-72RF.pdf

     

    Unfortunately the conversion from chinese to english always lack something.  This one never shows the thermisters. Nor does there parts book.

  • henlopen

    Member
    April 20, 2018 at 9:42 pm

    Thanks, the temperature on one occasion was 17 degrees and things were frozen solid, and some items had burst.  Will set the low temp alarm next time I’m over there and see if I can get to the bottom of this extremely random problem.  I believe the part number for the electronic thermostat has changed slightly, but don’t know if they were having problems with the original one or not.

  • fixbear

    Member
    April 21, 2018 at 6:13 am

    It is possible that the controller relay for the compressor welds  the points .  Make sure to check the compressor load amp’s to be in spec.The board relay is small for the load..

  • henlopen

    Member
    October 2, 2018 at 2:03 pm

    Well, the problem that I found was that the Evaporator Fan Motor had gone bad.  It would try to start about every 7 seconds but would not run.  Replacing it solved the problem.  It’s the simple things that we occasionally overlook that has a tendency to trip us up over time.  Comes with age, I guess.  Thanks all for your comments and help!

    Bill

  • fixbear

    Member
    October 2, 2018 at 3:51 pm

    That will definitely do it.  Why I carry a Zoom Spout oiler at all times.

  • partsgirl

    Member
    October 2, 2018 at 4:25 pm

    HA! I am staring at a box full as we speak!

Log in to reply.