Norlake cooler/freezer tripping multiple breakers
We have had an issue with our Norlake walk-in cooler/freezer tripping not only its own breaker but multiple others at the same time. This has stumped multiple electricians and HVAC techs so I figured I would see if any of you have run into a similar issue or have any advice. I want to preface this with the fact that this is in a newly remodeled store, about 3 years ago we started completely gutting the building down to the studs and redid everything. The panel was added during the remodel and all the equipment was brand new and only in use for about 2.5 years now.
For the last 2 months we have had this issue, on and off with almost no consistency of what leads up to it, with our Norlake unit tripping its own breaker and at the same time it trips, between 1 and 7 GFCI breakers on the opposite side of the panel trip with it. When this issue first started it only tipped the 1-3 GFCI breakers directly across from it on the panel but now it almost always all 7 GFCI breakers on the opposite side. Up until about a week and a half or two weeks ago it was happening about every other day. A local HVAC company replaced a contactor that had a middle leg that was sticking and both the fan motors which were starting to bind up. Everything was good so we assumed it was a surge coming down from the unit when the motor overheated due to the sticking middle leg.
Now it is starting again, on the 14th overnight the Norlake tripped but only itself nothing else. We call the HVAC company and they sent someone else down on the 15th to get a new set of eyes on it and see if they can solve it. He took amp draws, checked every connection on the unit, and even checked the capacitors to see if one of them was starting to go bad. He found one of the time clocks is starting to stick, which is a whole different issue on this 2.5 year old unit we have replaced it 3 times after this one, but nothing else. Now today, the 16th, the Norlake unit trips again during the afternoon and takes 5 of the GFCI breakers with it.
The equipment that is on the GFCI breakers are on the single phase side of the panel and 4 are 20 amp breakers and 3 are 30 amp.
The Norlake is a 3 ph circuit and on a 35 amp 3 pole Eaton BR335 breaker, the combined amp draw of both compressors turning on at once is 16 amps so well below our 35 amp breaker. The HVAC tech noticed the unit had some 40 amp fuses in the control box and suggested upsizing the breaker from 35 to 40 to see if we can get one of the fuses to blow to narrow down what is causing the breaker to trip. If we do upsize the breaker we will have to check the wire size that the electricians installed as it may require upsizing the wire, which during the current global situation we would prefer to not have to do as cash is king right now.
The electrician who installed the panel and did most of the electrical work during our remodel came and looked at the panel. He checked the voltages, amp draws, and condition of the wires inside, as far as he could tell everything is fine. He did say he was going to look into if the GFCI breakers not having a neutral wire could possibly cause them to trip if the Norlake unit sent a surge down to the panel but they are on 240V set up and do not need a neutral wire.
If you have made it through all that and understand it I would love your input if you have any sort of experience or idea as to what is causing our issue. At this point we are really at a loss of what to do or what tradesman should be the one to fix or find the issue as both have never seen this happen.